One other thought. The anticipated amperage draw affects the size (gauge) of the wire coming from the electrical panel to the hardwired charger. The change in wire size sometimes is important because the wire gets really stiff at lower gauge sizes (thicker wire). This might make it harder for your electrician to install the thicker wire in confined spaces or around tight bends.
A 40 amp circuit @ 240 volts will deliver 9.6 kW, but if you building in higher amperage for the future, then the gauge will go down. I’m not sure how load sharing would affect the gauge, but it also might be something to consider. Possibly Goldtrom can weigh in on all of this.
Here is what Perplexity AI fed back to me when I asked about this for my home state:
For typical (short run, under 100 feet) circuits in Arizona, the required wire gauge per the National Electrical Code (NEC) for copper conductors is:
• 40 amps: 8 AWG copper
• 50 amps: 6 AWG copper
• 60 amps: 4 AWG copper
For aluminum wire, use one size larger than copper:
• 40 amps: 6 AWG aluminum
• 50 amps: 4 AWG aluminum
• 60 amps: 3 AWG aluminum (sometimes 2 AWG is specified because aluminum has lower conductivity).
If your circuit run is over 100 feet or will be exposed to high ambient temperatures (very common in Arizona attics or outdoors), it’s recommended to size up one gauge to reduce voltage drop and account for derating due to heat.
Always verify with local building codes and a licensed electrician.
A 40 amp circuit @ 240 volts will deliver 9.6 kW, but if you building in higher amperage for the future, then the gauge will go down. I’m not sure how load sharing would affect the gauge, but it also might be something to consider. Possibly Goldtrom can weigh in on all of this.
Here is what Perplexity AI fed back to me when I asked about this for my home state:
For typical (short run, under 100 feet) circuits in Arizona, the required wire gauge per the National Electrical Code (NEC) for copper conductors is:
• 40 amps: 8 AWG copper
• 50 amps: 6 AWG copper
• 60 amps: 4 AWG copper
For aluminum wire, use one size larger than copper:
• 40 amps: 6 AWG aluminum
• 50 amps: 4 AWG aluminum
• 60 amps: 3 AWG aluminum (sometimes 2 AWG is specified because aluminum has lower conductivity).
If your circuit run is over 100 feet or will be exposed to high ambient temperatures (very common in Arizona attics or outdoors), it’s recommended to size up one gauge to reduce voltage drop and account for derating due to heat.
Always verify with local building codes and a licensed electrician.